Return enthalpy point for an ahu, boiler, or chiller measured in BTU/lb. Could apply to gas or liquid depending on equipment type.
outsideEnthalpy
Kind: Marker
Used With:point, unit
Outside air enthalpy point for an ahu measured in BTU/lb.
Alper ÜzmezlerThu 7 Jul 2011
That is a good tag.
Brian FrankMon 18 Jul 2011
Any other comments or votes?
John PetzeFri 22 Jul 2011
It’s always helpful to understand the intended usage of a tag and this post brings up a couple of items that I would like to discuss in more detail to insure we have an adequate shared understanding so we can pick the right approach.
The outsideEnthalpy tag that was proposed a while back had a fairly common use case. Enthalpy of outside air is typically used to measure the total heat (latent and sensible) of the air stream. Commercially available sensors combine dry bulb temperature and humidity to calculate enthalpy. Control systems then use this value to determine which air stream – outside air or return air will require the least energy to cool. As a commonly used item it makes sense to be available as a tag. Is the suggestion to include a tag for the “return air enthalpy” for this same application? Or are you suggesting at additional uses?
Enthalpy as an engineering measurement has a wide variety of uses with other gases and liquids, (chemical reactions, heat transfer calculations) but am not familiar with common use cases for them that are directly related to the subjects we are discussing. It would be helpful to offer some additional use cases here to help educate me (and others) so we can assess the best way to model this measurement. Also, do enthalpy sensors exist for those liquids or gases or would you typically derive the enthalpy value from a calculation of other sensed elements?
Just to confirm, the necessary units for enthalpy (BTU, Joules) are available in the library.
Aakash KumarWed 6 Jan 2016
My suggestion is to add an enthalpy tag. rather than outsideEnthalpy or returnEnthalpy. The enthalpy tag can be used in sync with return, outside to show return air or outside air enthalpy. Enthalpy sensors are available, but the points are usually calculated values using temperature and humidity. They can be tagged as sp or sensor based on the context.
Denis OConnorThu 7 Jan 2016
I agree with the proposal to make enthalpy a separate tag.
This addresses the point John raises regarding the use of enthalpy for substances other than air.
Jason WhittierThu 21 Jan 2016
Another vote to add enthalpy as a separate tag. This is something we are already doing and it would be great to see it part of the haystack library.
Jingkun GaoWed 2 Mar 2016
Agreed. I am currently use humidity temp energy together as enthalpy. Would be nice if this tag is available.
Leroy SimmsMon 11 Jul 2016
+1 for enthalpy as a separate tag. That keeps things flexible/standardized and prevents the need for a bunch of unnecessary tags (outsideEnthalpy, returnEnthaply, mixedEnthalpy, exhaustEnthalpy, ect.) In fact I had always assumed it was already a tag and surprised to see it is not.
R BreijerFri 16 Nov 2018
+1 for enthalpy seperate tag
Brent FleisherWed 21 Nov 2018
I concur there should be a singular tag for Enthalpy, and used together with other modifiers such as return air or outside air, etc. In my opinion, this is the simplest presentation and provides both clarity and flexibility.
Joseph FirrantelloMon 26 Nov 2018
Glad to see this is getting some renewed attention.
I'm currently setting up tagging for an install where multiple OA enthalpy points are available from the BAS (e.g., one per AHU plus a central "overall building" value). I have already been using a custom enthalpy tag for those points, and would support an official independent enthalpy tag based on my limited knowledge and use case.
Side note for thread context:
John Petze's comment from 2011 reminded me that the industry convention is to typically use the word enthalpy for specific enthalpy, for better or for worse. For example, the ASHRAE Terminology resource makes the distinction.
To move this forward it needs to get merged into a working group and someone needs to champion the actual definitions. Probably the best one is 514 which originally talked about enthalpy, but its not currently in the working proposal. Other options might be to make 626 more about air measurements rather just air quality. Or maybe 609 as part of AHUs.
Sean Hyrich Thu 7 Jul 2011
Would like to propose the following tags:
returnEnthalpy
Kind: Marker
Used With:
point
,unit
Return enthalpy
point
for anahu
,boiler
, orchiller
measured in BTU/lb. Could apply to gas or liquid depending on equipment type.outsideEnthalpy
Kind: Marker
Used With:
point
,unit
Outside air enthalpy
point
for anahu
measured in BTU/lb.Alper Üzmezler Thu 7 Jul 2011
That is a good tag.
Brian Frank Mon 18 Jul 2011
Any other comments or votes?
John Petze Fri 22 Jul 2011
It’s always helpful to understand the intended usage of a tag and this post brings up a couple of items that I would like to discuss in more detail to insure we have an adequate shared understanding so we can pick the right approach.
The outsideEnthalpy tag that was proposed a while back had a fairly common use case. Enthalpy of outside air is typically used to measure the total heat (latent and sensible) of the air stream. Commercially available sensors combine dry bulb temperature and humidity to calculate enthalpy. Control systems then use this value to determine which air stream – outside air or return air will require the least energy to cool. As a commonly used item it makes sense to be available as a tag. Is the suggestion to include a tag for the “return air enthalpy” for this same application? Or are you suggesting at additional uses?
Enthalpy as an engineering measurement has a wide variety of uses with other gases and liquids, (chemical reactions, heat transfer calculations) but am not familiar with common use cases for them that are directly related to the subjects we are discussing. It would be helpful to offer some additional use cases here to help educate me (and others) so we can assess the best way to model this measurement. Also, do enthalpy sensors exist for those liquids or gases or would you typically derive the enthalpy value from a calculation of other sensed elements?
Just to confirm, the necessary units for enthalpy (BTU, Joules) are available in the library.
Aakash Kumar Wed 6 Jan 2016
My suggestion is to add an
enthalpy
tag. rather than outsideEnthalpy or returnEnthalpy. The enthalpy tag can be used in sync withreturn
,outside
to show return air or outside air enthalpy. Enthalpy sensors are available, but the points are usually calculated values using temperature and humidity. They can be tagged assp
orsensor
based on the context.Denis OConnor Thu 7 Jan 2016
I agree with the proposal to make
enthalpy
a separate tag.This addresses the point John raises regarding the use of enthalpy for substances other than air.
Jason Whittier Thu 21 Jan 2016
Another vote to add
enthalpy
as a separate tag. This is something we are already doing and it would be great to see it part of the haystack library.Jingkun Gao Wed 2 Mar 2016
Agreed. I am currently use
humidity temp energy
together asenthalpy
. Would be nice if this tag is available.Leroy Simms Mon 11 Jul 2016
+1 for
enthalpy
as a separate tag. That keeps things flexible/standardized and prevents the need for a bunch of unnecessary tags (outsideEnthalpy, returnEnthaply, mixedEnthalpy, exhaustEnthalpy, ect.) In fact I had always assumed it was already a tag and surprised to see it is not.R Breijer Fri 16 Nov 2018
+1 for enthalpy seperate tag
Brent Fleisher Wed 21 Nov 2018
I concur there should be a singular tag for Enthalpy, and used together with other modifiers such as return air or outside air, etc. In my opinion, this is the simplest presentation and provides both clarity and flexibility.
Joseph Firrantello Mon 26 Nov 2018
Glad to see this is getting some renewed attention.
I'm currently setting up tagging for an install where multiple OA enthalpy points are available from the BAS (e.g., one per AHU plus a central "overall building" value). I have already been using a custom
enthalpy
tag for those points, and would support an official independententhalpy
tag based on my limited knowledge and use case.Side note for thread context:
John Petze's comment from 2011 reminded me that the industry convention is to typically use the word enthalpy for specific enthalpy, for better or for worse. For example, the ASHRAE Terminology resource makes the distinction.
However, it seems this issue has been decided in the unit system definition:
Brian Frank Sat 1 Dec 2018
To move this forward it needs to get merged into a working group and someone needs to champion the actual definitions. Probably the best one is 514 which originally talked about enthalpy, but its not currently in the working proposal. Other options might be to make 626 more about air measurements rather just air quality. Or maybe 609 as part of AHUs.