Thanks to Stephen Frank and other members of the EVSE working group for their support, which has led to the creation of this proposal.
We believe that this proposal would benefit Project Haystack's appeal to applications beyond EV charging, including building electrification and battery energy storage.
We request feedback from the Project Haystack community on this proposal. Thanks in advance for your support.
Background
At present, the scope of the phase tag is broad: it applies to electric voltage, current, power, energy, and power factor points in split-phase and 3-phase electric power systems. The appropriate enumerations for the phase tag differ by the physical quantity being measured, which makes validation difficult and can cause confusion. In addition, the existing enumerations do not cover all types of measurements that may apply.
The goals of the proposal are to improve the existing phase tag by:
Clarifying definitions for line measurements
Adding tags or enumerations for neutral and ground measurements
Using globally recognized enum values
Specifying line, line-to-neutral, or phase average measurements
This proposal takes these aspects into account and improves how Project Haystack defines the location of an electric point within an AC electric power system.
Proposal
Globally recognized enum values
Phase enum values "A", "B", "C", "AB", "BC", "CA", etc. are referenced in North America. However, other regions of the world do not use these references (e.g., Europe).
Therefore, we propose to instead use the following enum values:
L1
L2
L3
L1-L2
L2-L3
L3-L1
L1-N
L2-N
L3-N
In relation to three-phase systems in North America, "L1" = "A", "L2" = "B", and "L3" = "C".
Note: These enum values apply to split-phase and 3-phase phase electric power systems. However, split-phase electric power systems would not use "L3", "L2-L3", "L3-L1", and "L3-N" enum values.
New enums to replace the phase enum
We recommend to deprecate the phase tag. Instead, quantity-specific enum tags will define
lineVolt: "L1-L2", "L2-L3", or "L3-L1"
phaseVolt: "L1-N", "L2-N", or "L3-N"
lineCurrent: "L1", "L2", or "L3"
phaseCurrent: "L1-L2", "L2-L3", or "L3-L1"
linePower: "L1-L2", "L2-L3", or "L3-L1"
phasePower: "L1", "L2", or "L3"
linePf: "L1-L2", "L2-L3", or "L3-L1"
phasePf: "L1", "L2", or "L3"
lineEnergy: "L1-L2", "L2-L3", or "L3-L1"
phaseEnergy: "L1", "L2", or "L3"
These tags and enumerations are based on the common understanding of "line" vs. "phase" quantities when referencing, voltage, current, power, energy, and power factor in three-phase power systems.
In Xeto (and conceptually), the correct values for these quantity-specific tags can be defined by the following generic enums:
ElecLine, which has "L1", "L2", and "L3" values
ElecLineToLine, which has "L1-L2", "L2-L3", and "L3-L1" values
ElecLineToNeutral, which has "L1-N", "L2-N", and "L3-N" values
These generic enums are applied as follows:
lineVolt : ElecLineToLine
phaseVolt : ElecLineToNeutral
lineCurrent : ElecLine
phaseCurrent : ElecLineToLine
linePower : ElecLineToLine
phasePower : ElecLine
linePf : ElecLineToLine
phasePf : ElecLine
lineEnergy : ElecLineToLine
phaseEnergy : ElecLine
Note: volt is intentionally proposed instead of voltage for consistency and backwards compatibility with the existing volt tag, i.e. to avoid further breaking changes to Project Haystack.
A key motivation for this proposal was to balance having database queries that are simple, explicit, and understandable without either (a) listing all possible enumeration values in the query or (b) using and not syntax.
New marker tags for defining an average
We propose to introduce the lineAvg and phaseAvg tags which may be applied to electrical voltage, current, power, energy, and power factor points. When applied these tags indicate a point that is the average of line-to-line, line-to-neutral, or line sensor values (depending on the quantity).
Here are several examples of how these tags may be applied:
lineAvg applied to an electric current point is defined as the average of lineCurrent "L1", "L2", and "L3" sensor values
lineAvg applied to an electric power point is defined as the average of linePower "L1-L2", "L2-L3", and "L3-L1" sensor values
phaseAvg applied to an electric voltage point is defined as the average of phaseVolt "L1-N", "L2-N", and "L3-N" sensor values
phaseAvg applied to an electric current point is defined as the average of phaseCurrent "L1-L2", "L2-L3", and "L3-L1" sensor values
Ground marker tag for current measurements
There is no existing way to define a point that measures current on an electrical ground conductor. Therefore we propose to introduce the ground marker tag for this application.
Neutral marker tag for current measurements
At present, the phase: "N" tag is used to designate the current measured on a neutral conductor. Because the phase tag will be deprecated for use with electrical power measurement, we propose adding a neutral marker tag for this application.
Leroy SimmsWed 10 Apr
Thanks for putting this together Rick, I know the topic has been kicked around for awhile now, so it is nice to see someone taking the initiative to get it pushed forward.
Reading through I feel the following definitions seem very clear to me:
lineVolt: "L1-L2", "L2-L3", or "L3-L1"
phaseVolt: "L1-N", "L2-N", or "L3-N"
lineCurrent: "L1", "L2", or "L3"'
However, the phaseCurrent definition seems less clear to me:
phaseCurrent: "L1-L2", "L2-L3", or "L3-L1"
I'm not sure I am familar with a phase to phase current reading, and can't get my head around what that would represent. Are their applications for that I am just not aware of, or is that more of a carry over of the formatting of the voltage side?
Rick JenningsThu 11 Apr
Hi Leroy, thanks for the feedback.
phaseCurrent applies to 3-phase delta connected loads and single phase loads that connect line-to-line in a 3-phase power system. Also, there might be other real world applications for phaseCurrent involving power sources.
Example
There might be (40) single phase, 80A Level 2 AC EVSE fed by a 3-phase, 208Y/120V, 600A panelboard. Typically each of these EVSE have a current sensor and setpoint.
The load management algorithm that would be used to prevent overloads or exceeding demand limits requires an understanding of how each of these EVSE are connected. phaseCurrent provides that insight on point entities to allow for simple queries.
todd gibsonThu 11 Apr
Hi Rick, I agree thanks to you and the WG for the detailed proposal.
Could you provide some point examples which include all tags that would be applied? Curious how existing tags such as pf, avg, volt, current, energy, and power would be used along with the proposed concatenated tags that include these tags.
Thanks.
Rick JenningsThu 11 Apr
Hi Todd, thanks for the feedback.
We explicitly define every elec point proposed with Xeto specs here. Every spec has a meticulously thought about definition.
FYI, we have proposals brewing to clarify elec setpoints must be either max, min, or effective. The outcome of these proposals would still need applied to elec.xeto.
I realize Xeto is a new concept within Project Haystack and we have more work to do to make this understandable to the broader community. Let me try to explain this in another way.
For example, let's consider elec power points within AC power systems. Here are the possible location related tags with the new proposal:
total
lineAvg
phaseAvg
phasePower: "L1"
phasePower: "L2"
phasePower: "L3"
linePower: "L1-L2"
linePower: "L2-L3"
linePower: "L3-L1"
The power tag would still need to be applied regardless which location is applied. The avg tag can be applied if desired, but we think lineAvg and phaseAvg replace the need for it. Also, there is no need for the formerly defined phase tag.
I believe you would be able to use the original proposal with this example to get an idea of what this looks like for other elec point types pf, volt, current, and energy within AC power systems. Elec points for DC power systems are simpler and described in elec.xeto.
FYI, we intentionally decided not to propose non-aggregate tags, such as phaseDemand and lineDemand, to demand points at this time. The rationale behind this is our understanding that in practice only totaldemand is applicable or understandable.
We would appreciate any additional feedback you may have. Thanks in advance.
Rick Jennings Fri 5 Apr
Thanks to Stephen Frank and other members of the EVSE working group for their support, which has led to the creation of this proposal.
We believe that this proposal would benefit Project Haystack's appeal to applications beyond EV charging, including building electrification and battery energy storage.
We request feedback from the Project Haystack community on this proposal. Thanks in advance for your support.
Background
At present, the scope of the
phase
tag is broad: it applies to electric voltage, current, power, energy, and power factor points in split-phase and 3-phase electric power systems. The appropriate enumerations for thephase
tag differ by the physical quantity being measured, which makes validation difficult and can cause confusion. In addition, the existing enumerations do not cover all types of measurements that may apply.The goals of the proposal are to improve the existing
phase
tag by:This proposal takes these aspects into account and improves how Project Haystack defines the location of an electric point within an AC electric power system.
Proposal
Globally recognized enum values
Phase enum values "A", "B", "C", "AB", "BC", "CA", etc. are referenced in North America. However, other regions of the world do not use these references (e.g., Europe).
Therefore, we propose to instead use the following enum values:
In relation to three-phase systems in North America, "L1" = "A", "L2" = "B", and "L3" = "C".
Note: These enum values apply to split-phase and 3-phase phase electric power systems. However, split-phase electric power systems would not use "L3", "L2-L3", "L3-L1", and "L3-N" enum values.
New enums to replace the phase enum
We recommend to deprecate the
phase
tag. Instead, quantity-specific enum tags will definelineVolt:
"L1-L2", "L2-L3", or "L3-L1"phaseVolt:
"L1-N", "L2-N", or "L3-N"lineCurrent:
"L1", "L2", or "L3"phaseCurrent:
"L1-L2", "L2-L3", or "L3-L1"linePower:
"L1-L2", "L2-L3", or "L3-L1"phasePower:
"L1", "L2", or "L3"linePf:
"L1-L2", "L2-L3", or "L3-L1"phasePf:
"L1", "L2", or "L3"lineEnergy:
"L1-L2", "L2-L3", or "L3-L1"phaseEnergy:
"L1", "L2", or "L3"These tags and enumerations are based on the common understanding of "line" vs. "phase" quantities when referencing, voltage, current, power, energy, and power factor in three-phase power systems.
In Xeto (and conceptually), the correct values for these quantity-specific tags can be defined by the following generic enums:
ElecLine
, which has "L1", "L2", and "L3" valuesElecLineToLine
, which has "L1-L2", "L2-L3", and "L3-L1" valuesElecLineToNeutral
, which has "L1-N", "L2-N", and "L3-N" valuesThese generic enums are applied as follows:
lineVolt : ElecLineToLine
phaseVolt : ElecLineToNeutral
lineCurrent : ElecLine
phaseCurrent : ElecLineToLine
linePower : ElecLineToLine
phasePower : ElecLine
linePf : ElecLineToLine
phasePf : ElecLine
lineEnergy : ElecLineToLine
phaseEnergy : ElecLine
Note:
volt
is intentionally proposed instead ofvoltage
for consistency and backwards compatibility with the existingvolt
tag, i.e. to avoid further breaking changes to Project Haystack.A key motivation for this proposal was to balance having database queries that are simple, explicit, and understandable without either (a) listing all possible enumeration values in the query or (b) using
and not
syntax.New marker tags for defining an average
We propose to introduce the
lineAvg
andphaseAvg
tags which may be applied to electrical voltage, current, power, energy, and power factor points. When applied these tags indicate a point that is the average of line-to-line, line-to-neutral, or line sensor values (depending on the quantity).Here are several examples of how these tags may be applied:
lineAvg
applied to an electric current point is defined as the average oflineCurrent
"L1", "L2", and "L3" sensor valueslineAvg
applied to an electric power point is defined as the average oflinePower
"L1-L2", "L2-L3", and "L3-L1" sensor valuesphaseAvg
applied to an electric voltage point is defined as the average ofphaseVolt
"L1-N", "L2-N", and "L3-N" sensor valuesphaseAvg
applied to an electric current point is defined as the average ofphaseCurrent
"L1-L2", "L2-L3", and "L3-L1" sensor valuesGround marker tag for current measurements
There is no existing way to define a point that measures current on an electrical ground conductor. Therefore we propose to introduce the
ground
marker tag for this application.Neutral marker tag for current measurements
At present, the
phase: "N"
tag is used to designate the current measured on a neutral conductor. Because thephase
tag will be deprecated for use with electrical power measurement, we propose adding aneutral
marker tag for this application.Leroy Simms Wed 10 Apr
Thanks for putting this together Rick, I know the topic has been kicked around for awhile now, so it is nice to see someone taking the initiative to get it pushed forward.
Reading through I feel the following definitions seem very clear to me:
lineVolt
: "L1-L2", "L2-L3", or "L3-L1"phaseVolt
: "L1-N", "L2-N", or "L3-N"lineCurrent
: "L1", "L2", or "L3"'However, the
phaseCurrent
definition seems less clear to me:phaseCurrent
: "L1-L2", "L2-L3", or "L3-L1"I'm not sure I am familar with a phase to phase current reading, and can't get my head around what that would represent. Are their applications for that I am just not aware of, or is that more of a carry over of the formatting of the voltage side?
Rick Jennings Thu 11 Apr
Hi Leroy, thanks for the feedback.
phaseCurrent
applies to 3-phase delta connected loads and single phase loads that connect line-to-line in a 3-phase power system. Also, there might be other real world applications forphaseCurrent
involving power sources.Example
There might be (40) single phase, 80A Level 2 AC EVSE fed by a 3-phase, 208Y/120V, 600A panelboard. Typically each of these EVSE have a current sensor and setpoint.
The load management algorithm that would be used to prevent overloads or exceeding demand limits requires an understanding of how each of these EVSE are connected.
phaseCurrent
provides that insight on point entities to allow for simple queries.todd gibson Thu 11 Apr
Hi Rick, I agree thanks to you and the WG for the detailed proposal.
Could you provide some point examples which include all tags that would be applied? Curious how existing tags such as
pf
,avg
,volt
,current
,energy
, andpower
would be used along with the proposed concatenated tags that include these tags.Thanks.
Rick Jennings Thu 11 Apr
Hi Todd, thanks for the feedback.
We explicitly define every elec point proposed with Xeto specs here. Every spec has a meticulously thought about definition.
FYI, we have proposals brewing to clarify elec setpoints must be either
max
,min
, oreffective
. The outcome of these proposals would still need applied toelec.xeto
.I realize Xeto is a new concept within Project Haystack and we have more work to do to make this understandable to the broader community. Let me try to explain this in another way.
For example, let's consider elec power points within AC power systems. Here are the possible location related tags with the new proposal:
total
lineAvg
phaseAvg
phasePower: "L1"
phasePower: "L2"
phasePower: "L3"
linePower: "L1-L2"
linePower: "L2-L3"
linePower: "L3-L1"
The
power
tag would still need to be applied regardless which location is applied. Theavg
tag can be applied if desired, but we thinklineAvg
andphaseAvg
replace the need for it. Also, there is no need for the formerly definedphase
tag.I believe you would be able to use the original proposal with this example to get an idea of what this looks like for other elec point types
pf
,volt
,current
, andenergy
within AC power systems. Elec points for DC power systems are simpler and described inelec.xeto
.FYI, we intentionally decided not to propose non-aggregate tags, such as
phaseDemand
andlineDemand
, todemand
points at this time. The rationale behind this is our understanding that in practice onlytotal
demand
is applicable or understandable.We would appreciate any additional feedback you may have. Thanks in advance.