Per the discussion on Topic #97, I have publicly shared the documents for AHU point tagging ESI presented via webinar on 6/21/2013. They are available at the following link:
All of the tags presented have been used by ESI in the past and are part of our active customer projects.
Please use this forum post to discuss any modifications or enhancements to the proposed tags. If you would like to comment on a specific part of the proposal, please indicate which section of the proposal you are referencing in your response to keep everyone on the same page.
If anyone is having trouble accessing the documents, let us know and we will work on an alternative sharing method.
Nicholas Harker - ESI
Winston HetheringtonWed 3 Jul 2013
Nicholas : I have posted a revised version of your document, note the wh extension on my file.
I have opted to use "Supply" as opposed to "Discharge". My reason for the change is as follows. 1.Supply is the traditional term used for most installations in particular the term is used for conditioned air leaving the "Air Handling Unit".
The term "discharge" is required for specific intermediate applications and would create confusion as proposed. E.G, cooling or heating elements, air temperature as in cooling coil discharge temperature or heating coil discharge temperature. There are other cases where similar distinctions are required.
You will note I removed the term "Duct" from title. I saw your note about the inclusion of the word in an earlier post. In my view you have not attempted to indicate sensor location in other situations so the use of the word in this case appears to be inconsistent.
You will also note that I have removed many points which do not conform to usual use, such as enthalpy in exhaust air and setpoints for points not being controlled.
Nicholas Harker Fri 21 Jun 2013
Per the discussion on Topic #97, I have publicly shared the documents for AHU point tagging ESI presented via webinar on 6/21/2013. They are available at the following link:
Google Docs: Haystack Folder
All of the tags presented have been used by ESI in the past and are part of our active customer projects.
Please use this forum post to discuss any modifications or enhancements to the proposed tags. If you would like to comment on a specific part of the proposal, please indicate which section of the proposal you are referencing in your response to keep everyone on the same page.
If anyone is having trouble accessing the documents, let us know and we will work on an alternative sharing method.
Nicholas Harker - ESI
Winston Hetherington Wed 3 Jul 2013
Nicholas : I have posted a revised version of your document, note the wh extension on my file.
I have opted to use "Supply" as opposed to "Discharge". My reason for the change is as follows. 1.Supply is the traditional term used for most installations in particular the term is used for conditioned air leaving the "Air Handling Unit".
You will note I removed the term "Duct" from title. I saw your note about the inclusion of the word in an earlier post. In my view you have not attempted to indicate sensor location in other situations so the use of the word in this case appears to be inconsistent.
You will also note that I have removed many points which do not conform to usual use, such as enthalpy in exhaust air and setpoints for points not being controlled.